Integración domótica Systemair SAVE, gratuita y de código abierto
Systemair SAVE ventilation (VTR, VSR, VSC), local Modbus TCP: modes, temperatures, alarms.
Shows a Systemair SAVE heat recovery ventilation unit (VTR, VSR, VSC with the SAVE controller, SAVE Touch or SAVE Light panel) in Gladys, through Modbus TCP on your local network, without any cloud or account. Unofficial integration, not affiliated with Systemair. Never tested with a real device: it reads and writes the registers of Systemair's "Modbus Variable List" (revision 36, main board software 2.0) as the open-source home-assistant-systemair-modbus integration (Home Assistant) uses them; please report what you see.
Before you start
The SAVE controller speaks Modbus RTU on its connection board (RS485). Gladys reaches it over your network through one of:
- Systemair SAVE Connect (the Internet Access Module, art. 211243): choose "Systemair SAVE Connect" as the gateway. Systemair's list says every register is a holding register over Modbus TCP: everything is read with function 3, two registers a request, with a pause between requests.
- An RS485 to Modbus TCP gateway (Elfin EW11 and the like), wired to the Modbus terminals of the unit: choose "RS485 gateway". The input registers are read with function 4; if the gateway answers "illegal function", function 3 is used from then on (the status says so).
Then:
- Give the gateway a fixed IP address in your router; Modbus TCP is on port
502 unless you add another one (
192.168.1.50:8899). - Modbus TCP has no password: keep the gateway on a trusted network.
- The Modbus unit id is the Modbus address of the unit (Service, Communication, Modbus on its panel), 1 by default. An answer carrying another unit id is accepted.
- "Stop the ventilation" needs the setting "Allow manual fan stop" (register 1353) on the unit: without it, the unit refuses the stop and Gladys says so (the status shows it too).
- Enter the IP address of the gateway, pick the gateway type; save.
- Open the Discovery tab and add the unit.
One device, Systemair ventilation, with:
| Feature | Notes |
| Supply, extract and outdoor air temperatures | °C (the standard sensors of the unit) |
| Supply air setpoint | °C, read only |
| Extract air humidity | % (the standard sensor of the unit) |
| Supply and extract fan outputs | %, read only |
| Filter change in | days; not published when the unit reads 0 |
| Ventilation mode | list: auto, manual low / normal / high, crowded, refresh, fireplace, away, holiday |
| Current mode | text: auto, manual, stopped, crowded, refresh, fireplace, away, holiday, cooker-hood, vacuum-cleaner, cdi1-cdi3, pressure-guard |
| Ventilation on, fans running | read only, 1 = yes ("on" is 0 only in the manual mode at level off) |
| Alarm type A, B, C | read only, 1 = active |
| Manual stop allowed | read only, the setting of the unit |
| Start the ventilation (auto) / Stop | buttons |
A value outside the ranges of the list (sensor missing, -40 to 80 °C, 0 to 100 %) is never published: Gladys keeps the last known value. The fan speeds in RPM and the air flows are not published (no matching unit in Gladys). The accessory sensors (room, extra controller, CO2) are not read yet.
The unit is read every 60 s (30 s to 1 h), in about twelve small requests over one connection, with a pause between them (the touch panel shares the bus), closed after. The test button, a Discovery scan, a reconnection of Gladys or a restart of the integration never read it sooner than the interval. Commands and stops use the same pause between their requests when their deadline leaves room for it. Reads outside the interval:
- every command reads the unit right before writing, then reads the mode and the level back;
- "Stop the ventilation" and its resends;
- 5 s then 20 s after a command not confirmed, or after a stop that follows a start or a mode not confirmed;
- a new address, unit id or gateway saved is read at once.
The mode and the manual level are read first. When a later block fails (a Modbus exception, no answer, the connection closed, a wrong answer), the values read before are published anyway, and the failing block is tried again once an hour.
Commands
The mode and "Start the ventilation" are refused unless Allow the commands is on (off by default). No switch: a voice assistant's "turn everything off" never reaches the ventilation.
- Mode: auto, crowded, refresh, fireplace, away and holiday write the user mode request (register 1162, as the panel does); the timed modes last the time set on the unit. "Manual, low / normal / high" writes the manual level (1131), then the manual mode when the unit is not in it yet.
- Start the ventilation (auto) writes the auto mode. On a ventilation already running it writes nothing.
- Every command reads the unit right before writing (mode, manual level, fan level settings), writes nothing when the value already is right, and is confirmed only when the unit returns the echo of each write and then reads the value asked. A read back still showing the state before answers "not applied yet"; a command that may have reached the unit without being confirmed answers "sent, without confirmation": check the unit a few seconds later. A Modbus exception 1, 2 or 3 to the first write answers "refused" (not applied); any other answer "sent, without confirmation". A command whose first write cannot leave within 3.5 s is refused and nothing is sent.
- Also refused: when the fan level settings read differ from those learnt (see below), when /data cannot be read or written.
- The mode is refused while the ventilation is stopped (manual mode, level off: a mode would start it) and while a stop sent from Gladys is kept: press "Start the ventilation" first.
"Stop the ventilation" writes the manual level off (1131 = 0), then the manual mode (1162 = 2): the unit never enters the manual mode at another level. It does not depend on the option, on another command (a command not written yet is cancelled, and the second write of a manual level never leaves after it), on a read in progress or stuck (it is interrupted), on a failed read or a wait between two tries, on the fan level settings, on /data, nor on the configuration not read again from Gladys yet or made invalid since (it then goes to the address of the kept stop, else the last valid one kept in /data). It is tried again for 3.5 s after the press.
It can fail in these cases only, and the answer says so:
- no address known (never a valid one configured): "not sent";
- the gateway cannot be reached within 3.5 s: "stop not sent" (or "not sent yet" while it still tries); the stop is kept and sent again by the next reads;
- the connection closes, or no answer comes, before the unit answers: "stop handed to the gateway, no answer from the unit" (it may not have arrived); kept and sent again;
- the unit refuses the level off with a Modbus exception 1, 2 or 3 (3: "Allow manual fan stop" is off on the unit): "refused"; the manual mode is not sent, and the stop is not kept (neither pending nor sent again, the mode is not blocked; the status says so until the next press);
- the level off applied and the manual mode refused (exception 1, 2 or 3): said so; kept and sent again;
- any other Modbus exception (4 to 6…), a wrong echo, or the ventilation read back running: "stop sent, without confirmation"; kept and sent again.
The stop is then kept (in /data, with the address): it is never lifted by the time, only by "Start the ventilation" pressed (with the option), or when the ventilation is read running twice in a row after it was seen stopped (started from its panel). While it is kept, a read that finds the ventilation running before it was seen stopped sends the stop again: three sends at most, counting only the sends the unit answered (the echo of the level off, or a Modbus exception); a resend that found the gateway taken by another master, a closed connection or no answer is not counted.
A stop pressed while a start or a mode may still land (written, not confirmed, within its 90 s) is "sticky": it is sent again even after the ventilation was seen stopped, until a read after those 90 s sees it applied. A new press never inherits that from an older stop, and a start made later on the panel is never fought.
The status says where the stop is: not confirmed yet, kept, or given up after three answered sends. A stop that may not have landed when the integration stopped is sent again when it restarts, even before the configuration is read again. When the address was changed since, it goes to the new address (never written again to the old one); a stop already seen applied at the old address is forgotten.
Identity of the unit
Systemair's Modbus list gives no serial number nor MAC address. The device is therefore tied to the unit of the configuration, never to its IP address (a new address keeps the device and its history). A light fingerprint is learnt at the first read: the fan level settings (registers 1401 to 1410). When they change, another unit may answer at the address (or the settings were changed on the panel): the mode and the start are refused until "Test the connection" accepts the new settings (the stop does not depend on it). Two units with the same settings are not told apart.
/data
The integration keeps in /data/systemair-state.json (readable by itself
only): the time of the last read, the fingerprint, the last address and a
kept stop. Every read or write of it is bounded (2.5 s at most); a file that
cannot be read (or is not a regular file) is never taken for an empty one,
and the mode and the start are then refused; the stop waits 150 ms at most
for it before its first byte.
What the integration does not do
It never writes a setting, the clock, the week schedule, the setpoints, a password; it never resets the alarms, the filter counter nor the factory settings. Only registers 1131 (values 0, 2, 3, 4) and 1162 (values 1 to 7) are ever written.
Estos son los parámetros que Systemair SAVE te pide en su pantalla de configuración en Gladys.
| Your Systemair SAVE unit | section | No | Shows your Systemair SAVE heat recovery ventilation (VTR, VSR, VSC with the SAVE controller) in Gladys over Modbus TCP on your local network, without any cloud: through Systemair's Internet Access Module (SAVE Connect) or an RS485 gateway such as the Elfin EW11. Active mode, ventilation running, supply, extract and outdoor temperatures, supply setpoint, extract humidity, fan outputs, days before the filter change, A/B/C alarms. Enter the address of the gateway, save, then add the unit from the Discovery tab. The mode and the start can be changed from Gladys only if you allow the commands below; "Stop the ventilation" never depends on that option (see the guide). Gladys never touches the settings. Modbus TCP has no password: keep the gateway on a trusted network. Never tested with a real device. Not affiliated with Systemair. |
| IP address of the Modbus TCP gateway | string | Sí | An IPv4 address or a host name (port 502 unless you add one, for example 192.168.0.60:502). |
| Modbus unit id | number | No | The Modbus address of the unit (Service, Communication, Modbus on its panel): 1 unless you changed it. |
| Gateway | select | No | An RS485 gateway (Elfin EW11…): input registers read with function 4, function 3 if the gateway refuses it. SAVE Connect (Systemair's Internet Access Module): every register read as a holding register, two at a time, more slowly. |
| Allow the commands | boolean | No | Off by default. On: Gladys may change the mode (auto, manual low/normal/high, crowded, refresh, fireplace, away, holiday) and start the ventilation (auto mode); the mode is refused while the ventilation is stopped. Off: these commands are refused. "Stop the ventilation" never depends on this option. |
| Refresh interval (s) | number | No | How often the unit is read, in seconds. |
| Language of the feature names | select | No | Used for the names of the device and features added from now on, the status and the command errors. |
Cómo instalar Systemair SAVE en Gladys
- En Gladys, abre Integraciones: Systemair SAVE aparece en el catálogo junto a las integraciones nativas, con una insignia de comunidad.
ghcr.io/lm1lc3n7/gladys-systemair:0.1.1), la ejecuta en un entorno aislado del núcleo y genera la interfaz de la integración (dispositivos, descubrimiento y configuración). - Abre la pantalla de Configuración de la integración, rellena los parámetros y guarda.
- También puedes instalarla directamente desde la URL de su repositorio: https://github.com/LM1LC3N7/gladys-systemair.
Systemair SAVE requiere Gladys >=5.1.0. El catálogo de Gladys se actualiza cada hora, así que una nueva versión está disponible como máximo una hora después de publicarse.
Systemair SAVE es una integración externa: una integración comunitaria empaquetada como contenedor Docker y publicada en GitHub. Gladys la instala con un clic y la ejecuta en un entorno aislado del núcleo. La publica y mantiene LM1LC3N7, no el equipo principal de Gladys.