Integración domótica Dantherm / Pluggit, gratuita y de código abierto
Integración Dantherm / Pluggit para Gladys Assistant
Dantherm and Pluggit ventilation over local Modbus TCP: temperatures, mode, filter, alarms; stop.
Shows a Dantherm (HCV, RCV, HCH) or Pluggit (AP, iFlow) heat recovery ventilation unit in Gladys, through its Modbus TCP interface on your local network, without any cloud or account. Unofficial integration, not affiliated with Dantherm or Pluggit. Never tested with a real device: it reads and writes the registers of the manufacturer's Modbus table (the Pluggit controller, shared by both brands) as the open-source Dantherm integration of Home Assistant uses them; please report what you see.
Before you start​
  • The unit must be on your network (Ethernet) and reachable from Gladys on port 502 (Modbus TCP). Give it a fixed IP address in your router. Recommended firmware: 2.70 or 3.08 and later (those the Home Assistant integration asks for).
  • Modbus TCP has no password: keep the unit on a trusted network.
  • The Modbus unit id (slave address) is 1 unless you changed it.
  • The controller accepts three connections at once. The integration opens only one, and closes it after each read.
  2. Enter the IP address of the unit (port 502 unless you add one) and, if needed, the Modbus unit id; save.
  3. Open the Discovery tab and add the unit.
One device, Dantherm / Pluggit ventilation, with:
FeatureNotes
Ventilation modelist: automatic (demand), week program, manual level 1 to 4
Current modetext (stable English key): standby, manual, demand, week-program, away, summer, night…
Fan level0 to 4 (0: stopped)
Alarmtext: none, exhaust-fan, supply-fan, bypass, overtemperature, fire, fire-protection…; unknown-<code> for an unknown code
Alarm active1 = an alarm is active
Bypass dampertext: closed, in-progress, opening, closing, opened
Temperatures T1 to T4outdoor, supply, extract, exhaust; °C
Room temperature T5only when the unit lists the sensor (HRC2 component)
Humidity%; only with a sensor (0 is never published)
Air quality (VOC, CO2 equivalent)ppm; only with a VOC sensor (0 is never published)
Filter: days leftdays
Stop the ventilationbutton
Reset the filter timerbutton
Texts are never published as a measure: an unknown or out-of-range value is not published (Gladys keeps the previous one).
The unit is read every 60 s (30 s to 1 h), in ten requests on one connection, closed after. The test button, a Discovery scan, a reconnection of Gladys or a restart of the integration never read it sooner than the interval. Reads outside the interval:
  • each command reads the unit right before writing, then reads back what it wrote;
  • the stop and its resends;
  • 5 s then 20 s after a command not confirmed and after each stop;
  • a new address or unit id saved is read at once.
Stopping the ventilation​
The Stop the ventilation button sets the unit to manual mode, level 0 (what the Home Assistant integration calls stand-by). It first reads the current mode (1 s at most; read again on the next connection when the read fails): an away, summer, fireplace or night mode is ended first (ending the night mode, 0x8020, follows the Home Assistant integration and is still to check on a device). Then it writes level 0, manual mode, and level 0 again: cut after any of these writes, the stop never leaves the unit in manual mode at the level kept (up to 4).
It depends on no option, nor on another command running, nor on a read running (it cuts it), nor on the wait after an error, nor on the serial number, nor on the state file in /data, nor on the configuration sent by Gladys (the last unit configured is kept in /data). It cancels a mode command not sent yet; an older write already sent that would apply after it is caught by the read that follows (below). A refused or closed connection, a missing or wrong answer, a Modbus exception other than 1, 2 or 3 (device failure, busy) are tried again every 250 ms until 3.5 s after the press. It is confirmed only when the unit reads back stand-by, or manual mode at level 0: level 0 read in another mode (automatic, night, away…) is not a stop.
It can still answer without having stopped the ventilation in these cases:
  • no valid address, neither in the configuration nor in /data;
  • a value other than 1;
  • unit unreachable until 3.5 s after the press ("not sent", or "not sent yet" while it still tries);
  • a missing or wrong answer until the end, Modbus exception 1 to 3, or the unit read back running ("sent, without confirmation"); a unit that stays in an override, installer, fail-safe or defrost mode answers "the unit stays in … mode"; when the current mode could not be read in time, the answer says so (away, summer, fireplace or night were then not ended).
A second press during the first joins it. The stop is kept in /data:
  • not confirmed, it is sent again at the next start of the integration (before any read and even if Gladys does not answer) and by every read that shows the unit running, three times at most; then the status says the stop did not take (or that the unit stays in its mode) until the next press or a mode chosen;
  • confirmed, it is sent again once, when the first read begun after its write (5 s later) shows the unit running (an older write may still land). A restart made later from the panel or the app is never fought.
This guard is never lifted by the time. It is lifted only:
  • by a mode chosen from Gladys with the option on (right before its write; put back when the unit refuses that write with exception 1, 2 or 3);
  • after a confirmed stop, by two reads in a row showing the unit running when no resend is due: the unit was restarted outside Gladys (panel, app); the status says so. An unknown read between the two starts the count again.
Optional commands​
The mode is refused unless Allow the mode commands is on, and the filter reset unless Allow the filter reset is on (both off by default). No switch: a "turn everything off" of a voice assistant never reaches the ventilation.
  • Each command reads the unit right before writing (serial number, current mode, level and alarm; or the filter days left), writes nothing when the mode is already the one asked (unless a stop is guarded: it is then written, which lifts the guard), and is confirmed only when the unit answers each write and then reads back what was asked (for the filter: more days left than before; as many as before is not a confirmation). A command that may have reached the unit without being confirmed answers "sent, without confirmation": check the unit a few seconds later. A first write refused with Modbus exception 1, 2 or 3 answers "refused" and is not applied; other exceptions answer "sent, without confirmation". A command whose first write cannot leave within 3.5 s is refused and nothing is sent.
  • A mode chosen may restart a stopped unit: that is why it depends on the option. It is refused while a stop is running.
  • The mode is refused when the unit is in a mode Gladys does not set: away, summer, fireplace, night, external input or hygrostat override, installer, fail-safe, fail off, defrost. Change that mode on the unit or in its app.
  • The mode is refused in fire, overtemperature or unknown alarm (codes 12, 14, 16 and any code out of the list: overtemperature, fire, fire-protection, unknown-<code>). The code names follow the Home Assistant integration; the 2013 table names codes 12 to 15 differently, hence the three codes refused. An alarm register not filled (0xFFFFFFFF) reads unknown-4294967295: an active alarm and the mode refused, on the safe side.
  • Serial number: the integration keeps a salted fingerprint of the unit's serial number (never the number itself). If another number is read (unit replaced, or another device at the same address), its values are not shown, the status says so and the optional commands are refused until a press on Test the connection, which accepts the unit. An unreadable number is not "another unit". The stop does not depend on it.
  • If the state file in /data cannot be read, it is never written over and the optional commands are refused (not the stop). A command is also refused when the fingerprint learnt could not be written to /data.
Status and errors​
The status of the integration shows the current mode, the level, an alarm, the unit type and firmware, an unreachable unit (with the next try: 30 s, 1, 2 then 5 min, never less than the interval), a stop not confirmed, a restart outside Gladys, a configuration Gladys could not give (tried again at 5 s, doubled up to 5 min, without end; the reads go on with the configuration in use). A request refused by the unit (Modbus exception) leaves its values unknown; a measure always refused or silent is read again only once an hour.
Limits​
  • Never tested with a real device.
  • The unit type is shown by its number (the Dantherm and Pluggit tables give different names to the same number).
  • The manufacturer's table (2013) puts the unit type in the low byte of prmSystemID; the Home Assistant integration, used on current firmwares, reads it in the high byte: that reading is kept. The type is only shown.
  • Not yet: bypass, humidity and week program settings, alarm reset, fan speeds, operating hours.
Estos son los parámetros que Dantherm / Pluggit te pide en su pantalla de configuración en Gladys.
Your Dantherm or Pluggit unitsectionNoShows your Dantherm (HCV, RCV, HCH) or Pluggit (AP, iFlow) heat recovery ventilation in Gladys through its Modbus TCP interface (port 502) on your local network, without any cloud: temperatures, current mode, fan level, bypass, humidity, air quality, filter days left and alarm. Enter the IP address of the unit (fixed in your router), save, then add it from the Discovery tab. The "Stop the ventilation" button never depends on an option (see the guide for the cases where it can fail). The mode and the filter reset only work if you allow them below. Modbus TCP has no password: keep the unit on a trusted network. Never tested with a real device. Not affiliated with Dantherm or Pluggit.
IP address of the unitstringSíAn IPv4 address or a host name (port 502 unless you add one, for example 192.168.1.80:502).
Modbus unit idnumberNoThe Modbus slave address of the unit, 1 unless you changed it.
Allow the mode commandsbooleanNoOff by default. On: Gladys may set the mode (automatic, week program, manual level 1 to 4), which can restart a stopped unit; refused while the unit is in a mode Gladys does not set (away, summer, fireplace, night, override, installer, fail-safe, defrost) or in fire alarm. Stopping the ventilation never depends on this option.
Allow the filter resetbooleanNoOff by default. On: the "Reset the filter timer" button restarts the filter countdown of the unit (after you changed the filters).
Refresh interval (s)numberNoHow often the unit is read, in seconds.
Language of the feature namesselectNoUsed for the names of the device and features added from now on, the status and the command errors.
Cómo instalar Dantherm / Pluggit en Gladys​
  1. En Gladys, abre Integraciones: Dantherm / Pluggit aparece en el catálogo junto a las integraciones nativas, con una insignia de comunidad.
  2. Haz clic en Instalar. Gladys descarga la imagen Docker (ghcr.io/lm1lc3n7/gladys-dantherm:0.1.1), la ejecuta en un entorno aislado del núcleo y genera la interfaz de la integración (dispositivos, descubrimiento y configuración).
  4. También puedes instalarla directamente desde la URL de su repositorio: https://github.com/LM1LC3N7/gladys-dantherm.
Dantherm / Pluggit requiere Gladys >=5.1.0. El catálogo de Gladys se actualiza cada hora, así que una nueva versión está disponible como máximo una hora después de publicarse.
Dantherm / Pluggit es una integración externa: una integración comunitaria empaquetada como contenedor Docker y publicada en GitHub. Gladys la instala con un clic y la ejecuta en un entorno aislado del núcleo. La publica y mantiene LM1LC3N7, no el equipo principal de Gladys.