Integración domótica BTicino MyHOME, gratuita y de código abierto
Integración BTicino MyHOME para Gladys Assistant
BTicino / Legrand MyHOME through an OpenWebNet gateway: lights, shutters, heating. Unofficial.
This integration connects Gladys to a BTicino / Legrand MyHOME installation (SCS bus) through an OpenWebNet IP gateway (MyHOMEServer1, F454, F455, MH201, MH202...), on the local network: light points, dimmers, roller shutters and heating zones.
Unofficial, not affiliated with BTicino or Legrand. It has never been tested with a real installation: it was written from the OpenWebNet specification published by BTicino and the OWNd library, then tested against a simulated gateway. Feedback is welcome.
What you need​
  • An OpenWebNet gateway Gladys can reach (TCP port 20000 by default); give it a fixed address.
  • Its OPEN password if it asks for one (often 12345 out of the box; changed in MyHOME_Suite). Older gateways only take a password of digits; recent ones also take letters (HMAC SHA-1 or SHA-256 challenge).
  • Depending on the gateway, the IP address of Gladys must be in the allowed addresses ("IP range") of MyHOME_Suite.
  • Address of the gateway and port.
  • OPEN password: kept by Gladys in its database, never shown again, sent only to the gateway as the answer to its challenge, never written in the logs nor in /data.
  • Dimmers (optional): the A/PL addresses of the dimmers, e.g. 13, 0215, 12#4#01. A dimmer that reports its level is recognised by itself.
  • Light points read only (optional): the actuators that must never be switched from Gladys (a pump, a ventilation, a heater on a relay...). A light obeys voice assistants, scenes and "turn everything off": list here what must never be switched that way, then delete its old feature in Gladys.
  • Heating zones (optional): the numbers 1 to 99. A zone that reports its temperature is recognised by itself.
  • Thermostats: "Central unit" (a 3550 central unit, 99 or 4 zones: the commands go through it) or "Stand-alone thermostats".
  • Allow changing the set points from Gladys: off by default (see "Heating").
An entry of the lists that is not understood is ignored and counted in the status of the integration (it is not shown again).
The devices​
Click "Scan" in the Discovery tab. The integration reads the installation (the state of every light point and every shutter, the level of the dimmers, the temperature, set point and mode of the zones) and offers:
  • Light point: on / off; with the brightness on a dimmer. A point read only has a state only.
  • Shutter: open / close / stop; with the position (0 closed to 100 open) on a shutter that reports it ("advanced" shutters).
  • Heating zone: temperature, set point, mode (shown: off, manual heating, manual cooling, automatic; to choose: off and automatic).
The id of a device is its OpenWebNet address (light:12, shutter:0215, zone:3; a point behind an interface, 12#4#01, is 12-4-01): it never changes.
The changes made on the installation (buttons, app, program) come through the event session of the gateway. The whole installation is read again every 10 minutes, never twice within a minute (restart and button included). A reconnection of the event session reads the MAC address only; the full read keeps its calendar, except after a drop of more than 2 minutes (changes missed), when it is done at once. A value older than 2 hours is not published any more.
The commands​
The integration opens one command session at a time, one request at a time. Each command is written within 2.5 s or not at all, then the device is read back: Gladys gets its answer within 3.3 s:
  • confirmed: the read back shows the value asked;
  • not sent (nothing left): the gateway does not answer, was busy for too long, too many commands wait, or a stop of the same device came after it;
  • refused by the gateway (NACK): nothing was done;
  • sent, without confirmation: it left, but the read back does not show the value yet; the device is read again 5 s and 20 s later.
Before any command or read on a new session (after a disconnection, or a session closed), the MAC address of the gateway is read; the events are taken only once the MAC is known: another gateway at the same address stops the commands until "Test the connection" is clicked.
The light off, the shutter stop, the heating off​
Switching a light off (or a dimmer to 0), stopping a shutter and switching a heating zone off go before everything else: they depend on no option, no read before, nor on the MAC address read. A read the gateway leaves unanswered for 1 s is cut for them; the commands of the same device still waiting are cancelled (nothing asked before a stop leaves after it).
Gladys gets their answer within 3.3 s, whatever the gateway does; the work goes on afterwards. They are kept in /data from the click, with the state of the device at that moment, until a read (or an event) shows the device off or stopped. When they cannot leave, they are tried again every 250 ms for 3.3 s, then sent again before any other request as soon as the gateway answers (after a restart too), with no age limit and no cap. After a send the gateway answered without effect (NACK, or ACK without the read back showing the device stopped), the next one waits 10 s, 30 s, 1 min, 2 min, then 5 min each time: a refusing gateway is never flooded. Within the 3.3 s, a NACK waits 1 s before the next send. A send left unanswered is kept and sent again. A request that makes a protective wait more than 1.5 s is cut, even one that still answers.
A stop kept for later is dropped when a newer command of the same device left, or when the device changes on the installation to another state than the one at the click (a new movement, the other way, a light switched on again): it never stops a movement started afterwards by someone else. An echo of the same state lifts nothing. An off or a stop that the read back contradicts (the light still on, the shutter still moving) is sent once more within the 3.3 s, then by the follow-up reads (5 s, 20 s).
When the connection is stopped (password refused, invalid or missing, a gateway that did not prove it knows the password, another gateway at this address), they are kept without sending anything (never the refused password) and go first as soon as the password is fixed or "Test the connection" succeeds.
They are refused only in these cases:
  • the integration has no address of the gateway yet;
  • the point is read only in the configuration;
  • the value asked is not valid.
Heating​
Changing the set point of a zone (5 to 40 °C, by half degrees) or putting it back to automatic (the program of the central unit) is off by default. Once allowed, the option is checked again when asked, after the read of the zone and right before the write; the zone is read just before (when it does not answer, nothing is sent); a set point equal to the one read is not written again. These commands are refused while the zone is being switched off. The mode only offers "Off" and "Automatic": to heat, set a set point. A stand-alone thermostat has no "Automatic".
Switching a zone off (mode "Off") never depends on the option (its only refusals are listed above).
The password​
  • A refused password stops the connection: no new try until the password changes or "Test the connection" is clicked. Two sessions closed by the gateway right after the password count as a refusal. The refusal is kept in /data as an 8-bit salted mark (never the password): a restart does not send the same password again.
  • With the HMAC challenge, the gateway must prove it knows the password; otherwise the connection stops, and the same mark keeps a restart from answering it again.
  • A gateway that stays silent after the password is not a refusal: it is tried again with the usual waits.
Status and failures​
The status of the integration says "Connected" only when the event session is open and the gateway answered a read. A gateway that does not answer is tried again after 10 s, 30 s, 1 min, 2 min, then every 5 min. When /data cannot be read, it is never overwritten and it is read again every 10 s.
Limits​
  • No scenarios (CEN, WHO 15/25), energy (WHO 18), alarm, locks or gates in v1.
  • An "advanced" shutter whose position is unknown has open / close / stop only until it reports its position.
  • A gateway has a limited number of sessions: the integration normally keeps two (events and commands); the command session is closed after 20 s without a request.
Source​
The code is at https://github.com/LM1LC3N7/gladys-bticino-myhome (Apache-2.0). It ports part of OWNd (OpenWebNet-HA, Apache-2.0 since 2026-09-29) to JavaScript, see THIRD_PARTY_NOTICES.md.
Estos son los parámetros que BTicino MyHOME te pide en su pantalla de configuración en Gladys.
Your MyHOME installationsectionNoFor BTicino / Legrand MyHOME (SCS bus) installations with an OpenWebNet IP gateway (MyHOMEServer1, F454, F455, MH201, MH202...), on the local network. Light points, dimmers and shutters are found by reading the installation; heating zones are listed below. A light off, a shutter stop and a heating zone off are always sent; changing a set point is off by default. One command session at a time. Never tested with a real installation. Unofficial, not affiliated with BTicino or Legrand.
Address of the gatewaystringSíThe IP address (or name) of the OpenWebNet gateway; give it a fixed address in your router.
PortnumberNo20000 unless your gateway uses another one.
OPEN passwordsecretNoThe OPEN password of the gateway (12345 out of the box on many models; set in MyHOME_Suite), if it asks for one. Kept by Gladys in its database, never shown again, sent only to the gateway (as the answer to its challenge, never as such), never written in the logs.
DimmersstringNoOptional: the addresses (A/PL, as in MyHOME_Suite) of the dimmers, e.g. "13, 0215, 12#4#01". A dimmer that reports a level is found by itself.
Light points read onlystringNoOptional: the addresses of the lighting actuators that must never be switched from Gladys (a pump, a ventilation, a heater on a relay...). A light obeys Google, Alexa, the scenes and "turn everything off": list them here, then delete their old feature in Gladys.
Heating zonesstringNoOptional: the numbers (1 to 99) of the heating zones, e.g. "1, 2, 5". A zone that reports its temperature is found by itself.
ThermostatsselectNoWith a central unit (3550, 99 or 4 zones), the commands go to the zone through it; a stand-alone thermostat takes them directly (and has no program: no "Automatic").
HeatingsectionNoChanging the set point of a zone, or putting it back on the program of the central unit, drives the heating: it is off by default. Once allowed, every Gladys user, every scene and the Gladys app can do it (5 to 40 °C). The zone is read just before each change. Switching a zone off is always possible, allowed or not.
Allow changing the set points from GladysbooleanNo
Language of the namesselectNoUsed for the names of the devices and features found from now on.
Cómo instalar BTicino MyHOME en Gladys​
  1. En Gladys, abre Integraciones: BTicino MyHOME aparece en el catálogo junto a las integraciones nativas, con una insignia de comunidad.
  2. Haz clic en Instalar. Gladys descarga la imagen Docker (ghcr.io/lm1lc3n7/gladys-bticino-myhome:0.1.1), la ejecuta en un entorno aislado del núcleo y genera la interfaz de la integración (dispositivos, descubrimiento y configuración).
  4. También puedes instalarla directamente desde la URL de su repositorio: https://github.com/LM1LC3N7/gladys-bticino-myhome.
BTicino MyHOME requiere Gladys >=5.1.0. El catálogo de Gladys se actualiza cada hora, así que una nueva versión está disponible como máximo una hora después de publicarse.
BTicino MyHOME es una integración externa: una integración comunitaria empaquetada como contenedor Docker y publicada en GitHub. Gladys la instala con un clic y la ejecuta en un entorno aislado del núcleo. La publica y mantiene LM1LC3N7, no el equipo principal de Gladys.