Komfovent ventilation (C6, C6M, C8), local Modbus TCP: temperatures, fans, alarms; commands.
Shows a Komfovent heat recovery ventilation unit with a C6, C6M or C8 controller (Domekt, Kompakt, Verso…) in Gladys, through its Modbus TCP interface on your local network, without any cloud or account. Unofficial integration, not affiliated with Komfovent. Never tested with a real device: it reads and writes the registers described in Komfovent's Modbus manuals (C6 / C6M and C8, edition 24-10) as the open-source hass-komfovent integration (Home Assistant) uses them; please report what you see.
Before you start
- The unit must be on your network (RJ-45 socket of the controller), reachable from Gladys on port 502. Give it a fixed IP address in your router (factory address: 192.168.0.60).
- Modbus TCP has no password: keep the unit on a trusted network.
- The Modbus unit id is 1 by default. Komfovent's manuals give no unit id for Modbus TCP, and hass-komfovent sends none (its Modbus library then sends 1). If your unit does not answer, set the "Modbus RTU protocol ID" shown on its web page (Settings, Connectivity) in "Modbus unit id". An answer carrying another unit id is accepted.
Installation
- Install the integration from the Gladys store.
- Enter the IP address of the unit (port 502 unless you add one); save.
- Open the Discovery tab and add the unit.
What you get
One device, Komfovent ventilation, with:
| Feature | Notes |
|---|---|
| Supply, extract and outdoor air temperatures | °C |
| Panel temperature and humidity | only when panel 1 is connected |
| Supply and extract fan levels | % |
| Filter clogging, heat exchanger efficiency | %; the efficiency is not published while the fans are stopped |
| CO2 and extract humidity (sensors 1 and 2) | by the sensor type set on the unit; not published while the fans are stopped |
| Ventilation mode | list: away, normal, intensive, boost |
| Current mode | text: standby, away, normal, intensive, boost, kitchen, fireplace, override, holiday, air-quality, off |
| Unit on, fans running, ECO, AUTO | read only, 1 = yes |
| Fault (F alarm), warning (W alarm) | read only, 1 = active |
| Active alarms, alarm codes | a count; text none or F9, W1 (the manual's notation) |
| Start the unit / Stop the unit | buttons |
A value outside the ranges of the manual (sensor missing, panel not connected, the C8's "not used" values) is never published: Gladys keeps the last known value. The air flows (m³/h, l/s or % by controller and setting) are not published.
The unit is read every 60 s (30 s to 1 h), in five requests over one connection, closed after. The test button, a Discovery scan, a reconnection of Gladys or a restart of the integration never read it sooner than the interval. Reads outside the interval:
- every command reads the unit right before writing, then reads the value written back;
- "Stop the unit" and its resends;
- 5 s then 20 s after a command not confirmed, or after a stop that follows a start or a mode not confirmed;
- a new address or unit id saved is read at once.
The alarms, the sensor types and the firmware version are read last: when they fail (a Modbus exception, no answer, the connection closed, a wrong answer), the values read before are published anyway, and the failing block is tried again once an hour.
A humidity sensor is always named "Extract humidity", even when it is set on the unit as the outdoor humidity sensor (register 216, not read).
Commands
The mode and "Start the unit" are refused unless Allow the commands is on (off by default). No switch: a voice assistant's "turn everything off" never reaches the ventilation.
- Every command reads the unit right before writing (on/off, mode, status, controller type), writes nothing when the value already is right, and is confirmed only when the unit returns the echo of the write and then reads the value asked. A read back still showing the state before answers "not applied yet"; a command that may have reached the unit without being confirmed answers "sent, without confirmation": check the unit a few seconds later. A Modbus exception 1, 2 or 3 answers "refused" (not applied); any other exception answers "sent, without confirmation". A command that cannot be written within 3.5 s is refused and nothing is sent.
- Also refused: on a fault (F alarm), while the unit is stopping, when the controller type read differs from the one learnt (see below), when /data cannot be read or written.
- The mode is refused on a unit that is off or in stand-by (it would start it) and while a stop sent from Gladys is kept: press "Start the unit" first.
Stop the unit
"Stop the unit" writes 0 in the on/off register. It does not depend on the option, on another command (a command not written yet is cancelled), on a read in progress or stuck (it is interrupted), on a failed read or a wait between two tries, on the controller type, on /data, nor on the configuration not read again from Gladys yet or made invalid since (it then goes to the address of the kept stop, else the last valid one kept in /data). It is tried again for 3.5 s after the press.
It can fail in these cases only, and the answer says so:
- no address known (never a valid one configured): "not sent";
- the unit cannot be reached within 3.5 s: "not sent" (or "not sent yet" while it still tries);
- the unit answers a Modbus exception 1, 2 or 3: "refused";
- no answer, a wrong echo, or the unit read back on: "sent, without confirmation".
The stop is then kept (in /data, with the address): it is never lifted by the time, only by "Start the unit" pressed (with the option), or when the unit is read on twice in a row after it was seen off (started from its panel). While it is kept, a read that finds the unit on before it was seen off (or after a start that could still land) sends the stop again, three times at most; the status says so. A stop that may not have landed when the integration stopped is sent again when it restarts, even before the configuration is read again.
Identity of the unit
Komfovent's Modbus gives no serial number. The device is therefore tied to the unit of the configuration, never to its IP address (a new address keeps the device and its history). The controller type (C6, C6M, C8) is learnt at the first read; when it changes, another device may answer at the address: the mode and the start are refused until "Test the connection" accepts it (the stop does not depend on it). Two units of the same type are not told apart.
What the integration does not do
It never updates the firmware, never sets the clock, the setpoints or the schedules, never resets the alarms nor the filter counter.
Configuration settings
These are the settings Komfovent asks for in its configuration screen in Gladys.
| Setting | Type | Required | Description |
|---|---|---|---|
| Your Komfovent unit | section | No | Shows your Komfovent heat recovery ventilation with a C6, C6M or C8 controller (Domekt, Kompakt, Verso…) in Gladys through its Modbus TCP interface (port 502) on your local network, without any cloud: supply, extract, outdoor and panel temperatures, current mode, on/off, fan levels, filter clogging, heat exchanger efficiency, CO2 or humidity sensors, fault and warning, alarm codes. Enter the IP address of the unit (give it a fixed address in your router), save, then add the unit from the Discovery tab. The mode (away, normal, intensive, boost) and the start can be changed from Gladys only if you allow the commands below; "Stop the unit" never depends on that option (see the guide). Gladys never touches the firmware nor the settings. Modbus TCP has no password: keep the unit on a trusted network. Never tested with a real device. Not affiliated with Komfovent. |
| IP address of the unit | string | Yes | An IPv4 address or a host name (port 502 unless you add one, for example 192.168.0.60:502). |
| Modbus unit id | number | No | 1 unless your unit answers another one (then the "Modbus RTU protocol ID" of its web page, Settings, Connectivity). |
| Allow the commands | boolean | No | Off by default. On: Gladys may change the mode (away, normal, intensive, boost) and start the unit; both are refused on a fault (F alarm) or while the unit is stopping, and the mode is refused on a unit that is off or in stand-by. Off: these commands are refused. "Stop the unit" never depends on this option. |
| Refresh interval (s) | number | No | How often the unit is read, in seconds. |
| Language of the feature names | select | No | Used for the names of the device and features added from now on, the status and the command errors. |
How to install Komfovent in Gladys
- In Gladys, open Integrations: Komfovent appears in the catalog, next to the native integrations, with a community badge.
- Click Install. Gladys pulls the Docker image (
ghcr.io/lm1lc3n7/gladys-komfovent:0.1.1), starts it in a sandbox isolated from the core, and generates the integration's interface (devices, discovery and configuration). - Open the Configuration screen of the integration, fill in the settings, and save.
- You can also install it directly from its repository URL: https://github.com/LM1LC3N7/gladys-komfovent.
Komfovent requires Gladys >=5.1.0. The catalog inside Gladys refreshes every hour, so a new version becomes available at most one hour after its release.
Not running Gladys yet? It is free and open source: follow the installation guide to get started.
About external integrations
Komfovent is an external integration: a community integration packaged as a Docker container and published on GitHub, that Gladys installs in one click and runs in a sandbox isolated from its core. It is published and maintained by LM1LC3N7, not by the Gladys core team.
- Browse all integrations, native and community
- Build and publish your own external integration
- Source code on GitHub — source of this documentation