iDM heat pump Smart-Home-Integration, kostenlos und Open Source
iDM heat pumps (NAVIGATOR 2.0) over local Modbus TCP: temperatures, circuits, hot water; options.
This integration shows your iDM heat pump with the NAVIGATOR 2.0 controller in Gladys, through its Modbus TCP interface on your local network, without any cloud. If you allow it, it can also change the modes and setpoints.
Never tested with a real device. The integration follows iDM's Modbus TCP documentation and the Home Assistant integration
hacs-idm-heatpump, and was tested against a simulated heat pump only. Not affiliated with iDM Energiesysteme GmbH.
What you need
- An iDM heat pump with the NAVIGATOR 2.0 controller (the NAVIGATOR 1.0 and 1.7 have another Modbus table: they are not supported).
- Modbus TCP enabled: "Settings" → "Building management" → "Modbus TCP" set to "On". This setting is at installer level: ask your installer or iDM service. The web interface of the heat pump alone is not enough.
- A fixed IP address for the heat pump (reserve it in your router or set it in the network menu of the NAVIGATOR).
- Modbus TCP has no password: any device on your network can read and write the settings of the heat pump. Keep it on a trusted network, never exposed to the Internet.
| Field | Role |
| IP address of the heat pump | IPv4 or host name, port 502 unless you add one (192.168.1.60:502). |
| Modbus unit id | 1 on a NAVIGATOR. |
| Heating circuits | The letters of your circuits, A to G, separated by commas (A by default). |
| Allow the commands | Off by default (see below). |
| Hot water ceiling (°C) | The highest hot water setpoint Gladys may send: 65 °C by default, 65 °C at most. |
| Refresh interval | 60 s by default, 30 s to 1 h. |
| Language | Language of the device names, the status and the messages. |
Save, then add the heat pump from the Discovery tab. The "Test the connection" button reads the heat pump again, never more often than the interval.
What you see
- Operating mode (standby, automatic, away, holiday, hot water only, heating/cooling only) and heat pump state (standby, heating, cooling, hot water, defrost).
- Fault (heat pump locked), compressor running, charge pump running.
- Temperatures: outdoor and average outdoor, heat pump flow and return, heat source inlet and outlet, air intake, buffer tank, hot water (top, bottom, tap), hot water setpoint.
- For each configured circuit: mode, current state (off, heating, cooling), "normal" room setpoint, room, flow and flow target temperatures.
- When the heat pump gives them: humidity, electrical power (kW), solar temperatures (collector, collector return, charge).
A feature shows once a value of it was read. The special values of the NAVIGATOR are never published as measures: -1.0 on a temperature (sensor absent, except the outdoor temperature and the heat pump flow/return, always fitted), "not available" on a mode, -1 on the charge pump (published as "off"), a value out of range. As a consequence, on the optional sensors (air intake, source inlet and outlet, buffer, hot water, solar, circuits), a real temperature of exactly -1.0 °C is not published and Gladys keeps the previous value until the next read. Thermal energy (kWh) is not published.
The commands
Off by default. With "Allow the commands", Gladys may change:
- the operating mode (automatic, away, hot water only, heating/cooling only; "holiday" is shown only);
- the mode of a configured circuit (time program, normal, eco, manual heating, manual cooling);
- the "normal" room setpoint of a circuit, 15 to 30 °C by 0.5 °C;
- the hot water setpoint, in whole degrees, from 35 °C to the ceiling of the configuration (65 °C by default). Nothing above 65 °C is ever sent, whatever is typed.
Each command first reads the current value on the heat pump, writes nothing when it is already right, then reads the written value back: it succeeds only when the read back shows the value asked. Otherwise Gladys answers "sent, without confirmation" and reads the heat pump 5 s, 25 s and 60 s after (the NAVIGATOR applies a change in about 15 s).
A command is refused, nothing sent, when: the option is off (also checked right before the write), the value is out of range or above the ceiling, the circuit is not in the configuration, the current value could not be read, the configuration changed meanwhile, a stop was sent after it arrived, 16 commands are already waiting, or this setting was already changed 6 times in the last hour. That last limit protects the NAVIGATOR, which keeps these settings in a memory with limited write cycles (300,000 according to iDM); it never applies to a lower setpoint nor to a stop.
The commands go one at a time, in their order of arrival, on one connection. A scene setting several values sets them all: a command still waiting its turn after 3.5 s gets the answer "waiting" and goes within 15 s of the click, or not at all.
The stops
Setting the operating mode to Standby or a circuit to Off never depends on the commands option, the bounds, a read in progress or failing, a heat pump not read yet, nor a waiting command. A stop goes before anything; every command that arrived before it and has not left is dropped. A refused connection is tried again every 250 ms for 3 s; Gladys gets its answer within 3.5 s.
A stop not confirmed is kept in /data (with the value of before) for 3 minutes. During those 3
minutes, whatever the refresh interval, the integration checks the heat pump every 15 s: a stop that
could not leave is tried again at each check; a stop written but not shown yet is sent again (three
times at most, at least 20 s after it was sent) while the heat pump still shows the value of before.
A check never interrupts a command: it waits behind the commands (newer than it) and never writes over them; a new click on a stop interrupts a check and is always written and read back. After a restart, the check runs at once, before even reading the configuration. Each stop and each
resend is a write in the NAVIGATOR's EEPROM (four at most per click); stops are never limited by the
hourly quota of the commands.
A stop can fail or not be sent again in these cases:
- no valid address in the configuration (or, before the configuration is read, no heat pump read before): refused, nothing sent;
- the heat pump stays unreachable for 3 s: "not sent", then tried again every 15 s (and at a restart) while the 3-minute guard runs;
- the heat pump answers a Modbus exception: "refused" or "sent, without confirmation" depending on the code;
- the read back does not show the stop yet: "sent, without confirmation";
- it is no longer sent again once someone set another value on the heat pump meanwhile (the value of
before is kept in
/data; for a stop clicked before any read, the first value read after it), once a newer Gladys command for the same setting left, after 3 resends or after 3 minutes; /dataholding a guard that would end more than 3 minutes from now (a clock set back, on a device without a real-time clock): the guard is invalid and not replayed. A clock set back by less than that cannot be told from a recent stop: after a power cut on such a device, an older stop may be checked again at boot (sent again only while the heat pump shows the value of before it).
Gladys never starts the heat pump again by itself.
Known limits
- No serial number over Modbus: the device is tied to the integration, not to the IP address (changing the address keeps the device and its history), and another Modbus device at the same address would not be detected.
- Writing the photovoltaic surplus, the room-by-room zones, cascades, boosters and thermal energy are not supported yet.
Diese Einstellungen fragt iDM heat pump in seinem Konfigurationsbildschirm in Gladys ab.
| Your iDM heat pump | section | Nein | Shows your iDM heat pump with the NAVIGATOR 2.0 controller in Gladys through Modbus TCP (port 502) on your local network, without any cloud: temperatures, mode and state, fault, compressor, heating circuits, hot water, solar and power when the heat pump gives them. Have "Modbus TCP" set to "On" in the "Building management" menu of the NAVIGATOR (installer level; the web interface alone is not enough), enter its IP address, save, then add the heat pump from the Discovery tab. Modes and setpoints change only if you allow the commands below; hot water never above 65 °C. Standby and turning a circuit off never depend on that option (see the guide for when they can fail). NAVIGATOR 2.0 only. Modbus TCP has no password: keep the heat pump on a trusted network. Never tested with a real device. Not affiliated with iDM. |
| IP address of the heat pump | string | Ja | An IPv4 address or a host name (port 502 unless you add one, for example 192.168.1.60:502). |
| Modbus unit id | number | Nein | The Modbus slave address of the NAVIGATOR: 1. |
| Heating circuits | string | Nein | The letters of the heating circuits of your installation, A to G, separated by commas (for example A, B). |
| Allow the commands | boolean | Nein | Off by default. On: Gladys may change the operating mode, the mode of a heating circuit, the room setpoint of a circuit (15 to 30 °C) and the hot water setpoint (35 °C to the ceiling below). Off: these commands are refused. Standby and turning a heating circuit off never depend on this option. |
| Hot water ceiling (°C) | number | Nein | The highest hot water setpoint Gladys may send, 35 to 65 °C (65 °C by default). Nothing above 65 °C is ever sent, whatever is typed here. |
| Refresh interval (s) | number | Nein | How often the heat pump is read, in seconds. |
| Language of the feature names | select | Nein | Used for the names of the device and features added from now on, the status and the command errors. |
So installierst du iDM heat pump in Gladys
- Öffne in Gladys Integrationen: iDM heat pump erscheint im Katalog neben den nativen Integrationen, mit einem Community-Badge.
ghcr.io/lm1lc3n7/gladys-idm:0.1.2) herunter, startet es in einer vom Kern isolierten Sandbox und erzeugt die Oberfläche der Integration (Geräte, Erkennung und Konfiguration). - Öffne den Bildschirm Konfiguration der Integration, fülle die Einstellungen aus und speichere.
- Du kannst sie auch direkt über die URL ihres Repositorys installieren: https://github.com/LM1LC3N7/gladys-idm.
iDM heat pump benötigt Gladys >=5.1.0. Der Katalog in Gladys wird stündlich aktualisiert, eine neue Version ist also spätestens eine Stunde nach ihrer Veröffentlichung verfügbar.
iDM heat pump ist eine externe Integration: eine Community-Integration, die als Docker-Container verpackt und auf GitHub veröffentlicht wird. Gladys installiert sie mit einem Klick und führt sie in einer vom Kern isolierten Sandbox aus. Sie wird von LM1LC3N7 veröffentlicht und gepflegt, nicht vom Gladys-Kernteam.
