BSB-LAN Smart-Home-Integration, kostenlos und Open Source
Boilers and heat pumps through the local BSB-LAN adapter: temperatures, modes, optional commands.
Shows your boiler or heat pump with a Siemens controller (ELCO, Brötje, Baxi, MHG, Atlantic, Thision…) in Gladys through the BSB-LAN adapter, wired to the BSB, LPB or PPS bus of the controller: no cloud, no account, straight on your network.
Tested on a real installation (version 0.2.0: Siemens controller, two heating circuits, BSB-LAN): about fifteen commands on both circuits, modes, setpoints and protective commands, all confirmed. Not affiliated with the BSB-LAN project nor the manufacturers. It reads the JSON API of BSB-LAN as the python-bsblan library (used by Home Assistant) does.
Security: BSB-LAN speaks plain http. The passkey, the user name and the password travel in clear on your local network. Keep the adapter on a trusted network, never exposed to the Internet.
What you need
- A BSB-LAN adapter (Arduino Due or ESP32 board) with a firmware that gives
its JSON-API version (
/JV, 1.0 at least): recent BSB-LAN versions do. - Its IP address, preferably fixed (set it in your router).
- For the commands: writing to the bus allowed in the configuration of
BSB-LAN (
DEFAULT_FLAG 0, or writing turned on in its settings).
One "Heating (BSB-LAN)" device per adapter, recognised by its MAC address (it stays the same when the IP address changes). Each feature appears only once the controller gives its value:
| Feature | Parameter | Content |
| Heating mode | 700 | A list (command), see below |
| Heating mode (read) | 700 | Text: the real mode, an unknown one included |
| Heating circuit status | 8000 | Text of the controller ("Heating mode comfort"…) |
| Comfort setpoint | 710 | Thermostat, circuit 1, in °C (command) |
| Reduced setpoint | 712 | Thermostat, circuit 1, in °C (command) |
| Room temperature | 8740 | In °C |
| Flow setpoint | 8744 | In °C, circuit 1 |
| Flow temperature | 8743 | In °C, circuit 1 |
| Heating mode (circuit 2) | 1000 | A list (command), when the controller has it |
| Heating mode, read (circuit 2) | 1000 | Text |
| Heating circuit 2 status | 8001 | Text of the controller |
| Comfort setpoint (circuit 2) | 1010 | Thermostat, in °C (command) |
| Reduced setpoint (circuit 2) | 1012 | Thermostat, in °C (command) |
| Room temperature (circuit 2) | 8770 | In °C (probe), when circuit 2 has a room sensor |
| Flow setpoint / temperature (c. 2) | 8774/8773 | In °C |
| Outside temperature | 8700 | In °C |
| Hot water mode (command) | 1600 | A list: on, eco, off |
| Hot water mode | 1600 | Text: off, on, eco |
| Hot water status | 8003 | Text of the controller |
| Hot water setpoint | 1610 | Water heater, in °C (command, capped) |
| Hot water reduced setpoint | 1612 | Water heater, in °C (command, capped) |
| Hot water temperature | 8830 | In °C |
| Hot water pump running | 8820 | 0 or 1 |
| Boiler status | 8005 | Text of the controller |
| Boiler temperature | 8310 | In °C |
| Burner stage 1 signal | 7881 | 0 or 1 (read only) |
| Burner fault input S3 | 7870 | 0 or 1 (read only) |
| Last fault: date / code | 6800/6801 | Texts of the controller |
| Energy brought in (kWh) | 3113 | In kWh, a plain value (see below) |
| BSB <number> <name> | your pick | Extra parameters, read only (below) |
Circuit 2 appears only when the controller gives a value for its mode (1000); missing or "---", the integration then reads that one parameter only at each read. No option forces it: a circuit the controller does not give cannot be set, and the detection avoids writing to a circuit that does not exist. Hot water: its features appear only when the controller gives their values.
Devices created before version 0.2.0 keep their former "Reduced setpoint" and "Hot water reduced setpoint" features, read only (still updated); the settable ones come next to them, to add from the Discovery tab. New devices only get the settable ones.
7870, 7881, 6800, 6801, 8005 and 8310 are the numbers of the BSB-LAN parameter list; their exact form depends on the controller. Each value is checked as it is read: a value missing or of another form is not published.
Extra parameters (read only)
The Extra parameters to read field takes up to 10 BSB-LAN parameter
numbers separated by commas (for example 8326, 8338). Each one becomes a
read-only feature named "BSB <number> <name given by BSB-LAN>", from
BSB-LAN's answer at its first value: a temperature in °C becomes a probe,
another number a plain value (its unit in the name), a list or a text a
text. If the form of the value changes later, it is no longer published.
These parameters are never written: there is no free writing. Numbers
already read by the integration, repeated, over 10 or mistyped are ignored
and listed in the status of the integration. Each parameter lengthens each
read (the adapter queries the bus one parameter after the other).
Reading whole categories (/JK=ALL) is not offered: hundreds of
parameters, an answer too large, a bus read of several minutes, and as many
features in Gladys.
The outside and water temperatures, the room temperature of circuit 2 (8770) and the read-only setpoints are "probes": they do not count as the room temperature in Gladys (circuits 1 and 2 often heat two different zones; Gladys would average them). Only 8740 (circuit 1) does. 8770 without a value ("---": no room sensor on circuit 2, the usual case) is read again only every 10 minutes, not at every read. If you typed 8770 in "Extra parameters" with version 0.2.0, its "BSB 8770" feature keeps its value; the status suggests adding the new feature from Discovery and removing 8770 from the list. Once removed from the list, "BSB 8770" stays on the device without a new value: delete it from the device in Gladys. Read every 30 seconds by default (10 s to 10 min, configurable), a few parameters per request (the adapter queries the bus one parameter after the other).
On a PPS bus (simple room thermostats), the integration reads the mode, the setpoint, the room temperature and the outside temperature, read only in this version: the setpoint is then a plain "Room setpoint (read)" probe (parameter 15004), never a thermostat Gladys could set.
Energy: a plain value, not a billed meter
Parameter 3113 ("energy brought in") is a text of the controller ("7968 kWh") whose resolution and resets are not documented. Gladys would count every rise of an index as billed consumption: the value is therefore published as a plain sensor (the unit in its name), never as an energy index. It does not show in the energy monitoring of Gladys.
Setup
- In its configuration, enter the IP address of BSB-LAN (port 80 by
default; add
:portif it differs). - If your BSB-LAN has them, enter the passkey ("Passkey", the first part of its URLs, without the slashes), and the user name and password of its HTTP authentication. Both secret fields are kept by Gladys in its database, never shown again, sent only to the adapter.
- Save, then add the device from the Discovery tab.
The Test the connection button reads the adapter once (at most every 10 seconds), even after refused credentials.
Commands (off by default)
While Allow the commands is off, every command is refused, except Protection (frost protection) and hot water Off (below). Once on, Gladys may change:
- the heating mode of circuits 1 and 2: automatic (time program), comfort, reduced, protection (frost protection);
- the comfort setpoint of each circuit (710, 1010), to a tenth of a degree, never below its reduced setpoint (712, 1012) nor its protection setpoint (714, 1014), never above its comfort setpoint max (716, 1016), and always within 5–35 °C;
- the reduced setpoint of each circuit (712, 1012), to a tenth of a degree, never below the protection setpoint (714, 1014), never above the comfort setpoint (710, 1010) nor the max (716, 1016), within 5–35 °C;
- the hot water mode (1600): on, eco, off;
- the hot water setpoint (1610), in whole degrees, between the reduced setpoint (1612) and the maximum of the controller (1614), up to the ceiling;
- the hot water reduced setpoint (1612), in whole degrees, from 10 °C up to the lowest of the hot water setpoint (1610), the maximum (1614), the ceiling and 65 °C.
The sliders of the cards keep the fixed limits (5–35 °C, 10–65 °C): Gladys does not let an integration change the limits of a feature already created, and the range of the controller moves (the low bound of a comfort setpoint follows the reduced one). A value outside the range read just before is refused with that range, and the card goes back to the real value.
Protection and hot water Off: never held back
The Protection (frost protection) mode of circuits 1 and 2 and the hot water Off mode act as a stop: they leave even without the option, during a pause (429/5xx), after refused credentials, during another command, without a fresh read, and from an unknown mode. They pass before every queued request and cancel the commands not sent yet ("a protective command came after this one"). BSB-LAN serves one request at a time: they wait for the end of the one it serves. Still busy after 3.5 s, Gladys answers "the command is queued first and leaves as soon as it is free" and sends it as soon as possible (within 30 s).
Each one is kept (in /data too) until a read that left after the
click shows it applied. Every decision follows the order in which commands
arrive and requests leave, never the order of the answers:
- one that never left (BSB-LAN unreachable, too slow) is tried again every 10 seconds for as long as needed, never dropped with time;
- after it left, the first read of its parameter that left after it shows what "not applied" looks like (BSB-LAN may answer status 0, or 1 without applying it). While a periodic read still shows that mode, it is written again, once per periodic read (every 30 s by default), 3 times at most; it then stays kept and shown, never dropped with time;
- only these lift it: a later Gladys command of the same mode that
arrived after it and left without being refused (a status 2, a 401 or a
429 do not count), or another mode than the one left after it, read
twice in a row after it left (someone changed it at the boiler). A value
read before it never counts. An old stop read late from a
/datathat could not be read at start is set aside only if a command of its mode left unrefused, or a Protection of its mode was kept, in the meantime; - it belongs to its adapter (MAC address) and address: once a MAC address is read, it is written only to its own adapter. Two cases cannot be checked before writing, by choice (a stop is never held back for a read): after a restart, a kept one leaves first, before any read, when the address is its own (another device may have taken that address); and a click right after the address was changed, before the first read of the new adapter. A kept stop whose address changed waits for the MAC of the adapter, leaves right after the read that shows it, and is held, said in the status, if another one answers;
- while credentials are refused, it waits for new credentials or the "Test the connection" button;
/datais never waited for on this path: a slow or stuck disk holds nothing, and a/datathat cannot be read is never overwritten (read again later; a kept stop it holds is dropped if a command of its mode was made since). The status says how many are waiting, not yet seen applied, or held for another adapter.
They are refused only when they cannot leave: no adapter configured, a PPS bus, another adapter read at the address (another MAC address), BSB-LAN unreachable (then kept and tried again, see above), or BSB-LAN refusing the write (read-only parameter: status 2).
BSB-LAN must also allow writing to the bus, and name its bus BSB or LPB:
otherwise the configuration screen says so and the commands are refused.
To know whether writing is allowed, the integration first reads the access
BSB-LAN gives each parameter in its answer (readwrite: 0 read/write, 1
read only, 2 write only): it folds in the write setting of BSB-LAN and the
parameters the controller locks. Without it, it follows the buswritable
field of /JI (1, 2, "Yes", "RW"…: allowed; 0, "No", "RO"…: read only; any
other value: unknown, commands refused). Up to version 5.1.18, BSB-LAN prints
that field wrongly (a decimal number printed as an integer: often 0 while
writing is allowed): it is then never believed.
Hot water ceiling: 65 °C by default
Hot water scalds in seconds. Gladys therefore never sets the hot water above 65 °C by default. The Hot water ceiling setting lowers it, from 40 to 65 °C; it is never possible to go above 65 °C, whatever is typed. The controller's own nominal maximum (1614), read before each command, still applies when it is lower. A setpoint above the ceiling is refused on arrival, never sent; the ceiling is checked again after the fresh read and right before the request leaves (a ceiling lowered during a command stops it). The maximum (1614), the anti-legionella function and the time programs are never changed.
What the ceiling does not do:
- lowering the ceiling does not lower a setpoint already higher in the controller (set on the boiler, or earlier): it only limits what Gladys sends. Lower it yourself if needed;
- the anti-legionella function of the controller (1640 to 1648) heats the water to its own setpoint, possibly above the ceiling: Gladys neither sets it nor prevents it.
What Gladys never does
- Leave an unknown mode of the controller, except to Protection: the command is refused, the controller keeps control. The "Heating mode" list then keeps the last known choice (an unknown mode is not in it): look at "Heating mode (read)", which always shows the real mode.
- Offer a switch: the mode is a list, the setpoints are thermostats; a "turn everything off" (Gladys, Google Home, Alexa, HomeKit) never reaches the heating. A scene can change the mode or a setpoint, only through an explicit action and if the commands are allowed. Beware: the AI chat of Gladys (MCP) can create and run such a scene.
How a command leaves
Before each command (Protection and hot water Off aside), the integration first reads the adapter again
(/JI): it must have the MAC address of the device and a BSB or LPB bus,
and the fresh read must give the parameter as writable, otherwise nothing is sent (another adapter that took the
IP address is never commanded). Then it reads again the current value
and the range the controller allows, and decides on that read only; no other
request runs between that read and the write, and the option (and the
ceiling) is checked again right before the request leaves. A missing value
or range refuses the command. A value already in place is not sent again. A
command that cannot leave within 3.5 seconds is refused unsent; Gladys gets
its answer within its 5 seconds. BSB-LAN accepts a write with a status 1;
the integration then reads the parameter again and says success only
when that read shows the value asked (still the previous one: "read again
just after, still the previous one"; not read in time: "sent, without
confirmation"). A status 2 (read-only parameter) gives "BSB-LAN refused the command"; without
a clear confirmation (silence, dropped connection, 5xx error, status 0),
Gladys shows "Command sent, without confirmation": check the value, read
again 5 and 20 seconds later. One command at a time, and at least 3 seconds
between two writes. A command that arrives while another one runs (or
within those 3 seconds) waits and leaves after it, with its own
fresh read and every check again (the option, the hot water ceiling, the
range, a pause, the adapter); Gladys then answers "this one waits and is
sent after it". One that cannot leave within 30 seconds is dropped, not
sent. At most one waits per setting: a newer value of the
same setting replaces it. A Protection or hot water Off that arrives after
it drops it (never sent after a protective command), and so does a
restart of the integration. Protective commands never wait behind it.
After a command refused before it left, cancelled, dropped or read back
unchanged, the card shows the value read again at once (Gladys otherwise
keeps the value typed). The exception: an earlier command of the same
setting is still "sent, without confirmation" and that setting was not
read since; then the card waits for the first read.
After "sent, without confirmation", the controller may have applied the value. Until 10 minutes after the last command of that setting (the write, or a later one refused), no value read before the write is republished on that setting nor on the read-only features showing the same parameter (the mode as text, the old reduced setpoints). This holds after a reconnection to Gladys, an edit of the device, or a later command of the same setting refused before its read. The next read of that setting settles it: 5 and 20 seconds later, or the first one after a pause.
In both cases the first read of that setting made after the write (or the refusal) publishes it even when unchanged. If it fails too (adapter unreachable), the first read that succeeds does, within 10 minutes of the last refusal; never after a confirmed success.
In the logs, a command waiting behind another one and a waiting command
replaced by a newer value are information lines, each with its own text;
the other refusals are warnings. When Gladys cannot be reached (an
update, a restart), "Sending to Gladys failed" is logged once, once more
for each new cause (3 at most, a cause that only differs by its numbers is
the same), then "Sending to Gladys works again". The times of the log lines are in UTC
(the Z at the end), as the logger of the Gladys integration SDK writes them.
Errors and limits
- BSB-LAN unreachable: "Heating mode (read)" shows "BSB-LAN unreachable", the device turns unreachable, the other values keep their last one. Retried after 30 s, 1, 2 then 5 minutes, never faster than the interval.
- Credentials refused (HTTP 401 or 403): the integration stops and says
so; next tries after 15 min, 1 h, 6 h then every 24 h, never in a loop,
even after a restart (the stop is kept in
/data). Saving other credentials or pressing "Test the connection" tries at once. - BSB-LAN busy or failing (HTTP 429 or 5xx): a pause of 1 minute to 6
hours (from
Retry-After), kept in/data, for reads and commands alike. - Commands failing when BSB-LAN also publishes in MQTT: the adapter serves one request at a time. If BSB-LAN publishes in MQTT to a broker (for Home Assistant, for example), that load can make the commands of Gladys run out of time ("answered too slowly", "sent, without confirmation (timeout)"; these messages then remind it). Turn MQTT off in BSB-LAN, or lighten it (a longer interval, fewer parameters), and keep a reasonable refresh interval in Gladys (30 s or more). Seen on a real installation: with MQTT off and 30 s, every command went through. The deadlines of the commands and the 3 s between two writes stay as they are (they protect the heating).
- "The state could not be saved in /data (EACCES)" in the logs, and
"/data is not writable" in the status (said from the start: a test file
is written then removed when the integration starts, the state itself is
left as it is): the data folder Gladys gives the integration is not
writable by its user (
node, uid 1000). It needs both owner 1000 and write permission for it. Gladys creates it and gives it to uid 1000 when it creates the container; when that fails (Gladys log "Unable to prepare the data folder of integration …", a disk mounted without owners such as NFS or CIFS, Docker in rootless or user-namespace mode, a Gladys data folder mounted elsewhere than the folder of its database), the folder stays owned by root. Seen on a Synology NAS (DSM, Container Manager): the folder belonged to 1000 but wasdr-xr-xr-x, with a Synology ACL (the+ofls -l) giving only read access to "everyone";chownchanged nothing,chmod 755fixed it. The integration keeps working, commands and Protection / hot water Off included: they are never refused nor dropped because of/data. Only a restart forgets what/datawould keep: a pause after HTTP 429/5xx, the wait after refused credentials, and the protective commands not yet seen applied (they are not sent again after the restart). To fix it, on the Gladys host, for the folder/var/lib/gladysassistant/external-integrations/ext-lm1lc3n7-gladys-bsblan(in the folder of your Gladys data if it is elsewhere):ls -ldit, thensudo chown 1000:1000it if the owner is not 1000, andsudo chmod 755it if it is not writable by its owner (on Synology, also check its ACL in File Station or withsynoacltool); then restart the integration. The status note goes once a write works. - "The state file in /data could not be read" in the status: the file
bsblan-state.jsonis there but cannot be read (its rights, or a damaged file). It is never rewritten: fix its rights (owner 1000,chmod 600), or delete it (a pause, the wait after refused credentials and the protective commands it held are then forgotten), then restart the integration. - Wrong passkey, or Gladys's IP not among the trusted addresses: from the firmware source, BSB-LAN then closes the connection without any answer (never a 404). The integration cannot tell it from an unreachable adapter: the "unreachable" status reminds it. Check the passkey and, if BSB-LAN limits the allowed addresses, add the one of Gladys.
- Firmware too old (no
/JV): not supported, as python-bsblan; read again every 30 minutes. - Controller in °F: its temperatures are not shown (the features are in °C).
- One adapter per integration, heating circuits 1 and 2.
- Not yet: cooling, time programs, commands on a PPS bus, circuit 3 (its room temperature, 8800, included).
- The logs never hold the passkey, the user name, the password nor the
answers of BSB-LAN;
/datakeeps only the pause, the stop on refused credentials and the kept protective commands, never a secret.
Credits
Ported from python-bsblan (Willem-Jan L. van Rootselaar and contributors, MIT, version 6.1.10), the library of Home Assistant's BSB-LAN integration. Apache-2.0 license.
Diese Einstellungen fragt BSB-LAN in seinem Konfigurationsbildschirm in Gladys ab.
| Your BSB-LAN adapter | section | Nein | Shows your boiler or heat pump with a Siemens controller (ELCO, Brötje, Baxi, MHG, Atlantic…) in Gladys through the BSB-LAN adapter wired to its BSB, LPB or PPS bus, on your local network, without any cloud: heating circuits 1 and 2 (the second when the controller has it), hot water, boiler, outside temperature. Enter the IP address of the adapter (give it a fixed address in your router), save, then add the device from the Discovery tab. Tested on a real installation (Siemens controller, two circuits). Not affiliated with the BSB-LAN project nor the manufacturers. |
| IP address of BSB-LAN | string | Ja | An IPv4 address or a host name (port 80 unless you add one, for example 192.168.1.50:8080). Plain http: BSB-LAN has no https. |
| Passkey and credentials (optional) | section | Nein | Fill them only if they are set in the configuration of BSB-LAN: the passkey ("Passkey", the first part of its URLs) and the user name and password of its HTTP authentication. They go to the adapter in clear on your local network (BSB-LAN has no https). |
| Passkey (optional) | secret | Nein | Kept by Gladys in its database, never shown again, sent only to the BSB-LAN adapter. |
| User name (optional) | string | Nein | |
| Password (optional) | secret | Nein | Kept by Gladys in its database, never shown again, sent only to the BSB-LAN adapter. |
| Commands | section | Nein | By default Gladys only reads. Once allowed, the dashboard, the scenes and the voice assistants can change the modes and the comfort and reduced setpoints of heating circuits 1 and 2, the hot water mode and setpoints, within the range the controller gives, the hot water never above the ceiling below. Protection (frost protection) and hot water Off are never held back, even when not allowed. BSB-LAN must also allow writing to the bus in its own configuration. |
| Allow the commands | boolean | Nein | Off by default. Off: every command is refused, except Protection (frost protection) and hot water Off. |
| Hot water ceiling (°C) | number | Nein | Scalding risk: Gladys never sets the hot water above this temperature. 65 °C by default, from 40 to 65 °C (never more than 65 °C, whatever is typed; the controller's own maximum applies when lower). |
| Refresh interval (s) | number | Nein | How often BSB-LAN is read, in seconds. The adapter serves one request at a time: if it also publishes in MQTT (for Home Assistant, for example), turn that off or lighten it, and keep 30 s or more here, or the commands may run out of time. |
| Extra parameters to read (read only) | string | Nein | Optional: up to 10 BSB-LAN parameter numbers, separated by commas (for example 8326, 8338). Each one becomes a read-only feature, named and typed as BSB-LAN describes it; never written. Every parameter adds time to each read of the bus. |
| Language of the feature names | select | Nein | Used for the names of the device and features added from now on, for the mode texts and for the command errors. |
So installierst du BSB-LAN in Gladys
- Öffne in Gladys Integrationen: BSB-LAN erscheint im Katalog neben den nativen Integrationen, mit einem Community-Badge.
ghcr.io/lm1lc3n7/gladys-bsblan:0.3.3) herunter, startet es in einer vom Kern isolierten Sandbox und erzeugt die Oberfläche der Integration (Geräte, Erkennung und Konfiguration). - Öffne den Bildschirm Konfiguration der Integration, fülle die Einstellungen aus und speichere.
- Du kannst sie auch direkt über die URL ihres Repositorys installieren: https://github.com/LM1LC3N7/gladys-bsblan.
BSB-LAN benötigt Gladys >=5.1.0. Der Katalog in Gladys wird stündlich aktualisiert, eine neue Version ist also spätestens eine Stunde nach ihrer Veröffentlichung verfügbar.
BSB-LAN ist eine externe Integration: eine Community-Integration, die als Docker-Container verpackt und auf GitHub veröffentlicht wird. Gladys installiert sie mit einem Klick und führt sie in einer vom Kern isolierten Sandbox aus. Sie wird von LM1LC3N7 veröffentlicht und gepflegt, nicht vom Gladys-Kernteam.